| cedstevo | "breaker trips" , posted Mon 9 Jun 23:24  
I have a Goodman heat pump combo. It stopped working last week. searching thru the forums I decided to do some troubleshooting. whenever I send to cool the breaker trips. The fan will spin slowly if the t-stat is set to off. I started disconnecting wires from the contactor and with the red lead that looks to go to the condenser disconnected the breaker wont trip. Do I have a bad condenser? Would it be cheaper to replace the condenser or the entire unit? thanks, ced.
| | Replies:
|
| Houston204 
| "Re(1):breaker trips" , posted Tue 10 Jun 00:39  
It would be advisable and more reliable to replace the entire unit. You can get a available 10 year parts and labor warranty. You will only get 1 year parts and probably much less than that labor, only replacing the compressor.
You would need a new matching fancoil when replacing a heatpump, so it wouldn't be cheaper, initially.
"Tip of the Day" Remember to remove power first.
|
| | cedstevo | "Re(2):breaker trips" , posted Tue 10 Jun 18:41  
I got 0 ohms yellow and red wire to ground open black to ground.
|
| | Houston204 
| "Re(3):breaker trips" , posted Tue 10 Jun 23:47  
0 ohms to ground would be a bad thing. Does this red wire only connect to the compressor in this test?
"Tip of the Day" Remember to remove power first.
|
| cedstevo | "Re(1):breaker trips" , posted Mon 9 Jun 23:44  
I meant compressor in above post.
|
|
|
|  |
|