A/C trips circuit, fan continues to blow. - http://www.hvacmechanic.com/ Forums


Original message

whaddajoke

71.175.55.188

"A/C trips circuit, fan continues to blow." , posted Tue 10 Jun 11:18user profileedit/delete messagepost reply


Have a Rheem model RAKA-048JAZ air conditioner. The problem: The ac comes on fine (blower and condenser seem to be working, getting cold air). After 10 min, the circuit in the house trip and the condensor fan stops. Blower (which is part of the furnace) continues to blow. At the thermostat, if I turn the temp way up so everything should shut off (this is when the circuit to the condenser is tripped), the blower continues to blow. When I turn the thermostat off, the blower continues to blow. The only way I can turn the blower of is to disconnect the thermostat. OK...so I replaced the thermostat and the new one is doing the same thing. I cleaned the fins and coils on the compresser and cleaned out the electronics on the compressor. Still, it works for 10 minutes and then trips. Any ideas? Thanks.

 


Replies:

geo fan

69.119.0.185

"Re(1):A/C trips circuit, fan continues to blo" , posted Wed 11 Jun 20:56user profileedit/delete messagepost reply


your fan switch is on first of all switch it to auto
your breaker if its a problem that developed with out any body touching it your compresser is drawing high amps and will need to be replaced if its new you breaker could be low most companys will come out and tell you whats wrong for under a hundred bucks

ctd2b