Problem with A/C - http://www.hvacmechanic.com/ Forums


Original message

mikebobo

76.224.19.117

"Problem with A/C" , posted Wed 11 Jun 09:23user profileedit/delete messagepost reply


Had problem when the thermostat called for cool, the compressor kicked on but the blower fan would not start or would shut off. I disconnected the Y wire at control board as you had requested. There are two wires on the Y, one blue to the thermostat, and one white to the compressor. This time when it called for cooling, the blower fan did kick on, but the A/C compressor did not. Are you thinking control board?

Mike

 


Replies:

theduke03

24.250.18.179

"Re(1):Problem with A/C" , posted Wed 11 Jun 20:23user profileedit/delete messagepost reply


Hey Mike. What I meant was to disconnect Y from circuitboard but leave the 2 wires connected together (so outdoor unit will run). If blower stays on then it is definately the board.

"My dad was the most feared furnace fighter in Northern Indiana."

 

 

mikebobo

76.222.57.203

"Re(2):Problem with A/C" , posted Fri 20 Jun 09:00user profileedit/delete messagepost reply


With the wires connected both the compressor and the blower fan worked! I ordered a new board. Thanks for all your help! theduke03 is the best!

About your dad being a furnace fighter, what did he do? Was he furnace repairman? Being a fireman I'm interested.

Mike

 

 

theduke03

24.250.18.179

"Re(3):Problem with A/C" , posted Fri 20 Jun 19:42user profileedit/delete messagepost reply


Well I do agree that myself and a few other fellas here are the best. However my dad is not a furnacefighter. I stole that line from "A Christmas Story".

"My dad was the most feared furnace fighter in Northern Indiana."

 

new tech

71.230.161.49

"Re(1):Problem with A/C" , posted Wed 11 Jun 13:48user profileedit/delete messagepost reply


The wire you disconnected should have nothing to do with the blower not running. They lead to the contactor which acts as a switch for the outdoor unit. Intermitten problem. Does the board have a self diagnosis test terminal. Jump it out and run the test to see if all is well

 

 

theduke03

24.250.18.179

"Re(2):Problem with A/C" , posted Wed 11 Jun 20:30user profileedit/delete messagepost reply


quote:
The wire you disconnected should have nothing to do with the blower not running. ...
Actually new tech; Trane and Am. Standard furnaces will run fan on heat speed (med. or whatever) when G is energized. Then when Y is energized it will switch to high speed. If the blower shuts off with Y connected, but stays running with Y disconnected then that means that the board is unable to energize the high speed(cool) terminal.

"My dad was the most feared furnace fighter in Northern Indiana."