Help please! - http://www.hvacmechanic.com/ Forums


Original message

jw1

24.159.0.86

"Help please!" , posted Wed 11 Jun 11:47user profileedit/delete messagepost reply


How many faults are associated with contactor fault???
What would be the most likely if I replaced the fan motor on an outdoor unit????
Bryant
MODEL: 180ANA060-B
serial:1607E40484
PROD:180ANA060000DBAA

 


Replies:

new tech

71.230.161.49

"Re(1):Help please!" , posted Wed 11 Jun 13:45user profileedit/delete messagepost reply


Not sure if I understand your question. Did you replace the fan motor and now its not running which leads you to believe that there is a problem w/ the contactor?

 

 

Freon

68.214.135.45

"Re(2):Help please!" , posted Thu 12 Jun 13:49user profileedit/delete messagepost reply


On a simple AC condenser the contacor will power the compressor and fan motors. Motor problems could be due to the contactor, capacitor or the motor itself. You need to check each possibility CAREFULLY.

 

 

Houston204



98.196.66.53

"Re(3):Help please!" , posted Sun 15 Jun 16:47user profileedit/delete messagepost reply


On the Evolution control system, voltage present with no demand.

"Tip of the Day" Remember to remove power first.