| jellin | "unethical repairman ?" , posted Mon 16 Jun 14:42  
my old system is an Armstrong, 2 1/2 ton, 10 seer heat pump that was new in 1996. The windings in my old heat pump compressor went out causing the breaker to trip. A local hvac company came out and replaced the outside unit with a Weathering, 2 1/2 ton, 13 seer unit. I was told by the installer that it is a matched system but I dont see how it can be. The manufacturers warranty is void if the system is not matched properly. My old system is an Armstrong model # SHP10a30a-1b, the new outdoor unit is an Weatherking model # 13PJA30a01.
| | Replies:
|
| allen1980 | "Re(1):unethical repairman ?" , posted Mon 16 Jun 14:59  
no it isnt a match you cant use a 10 seer a-coil and a 13 seer cond.
|
| | Houston204 
| "Re(2):unethical repairman ?" , posted Tue 17 Jun 00:17  
I agree with Allen.