| rr man | "Replacing Janitrol hpt 18-60 thermostat" , posted Mon 16 Jun 21:30  
I have a Goodman self contained heat pump unit using a Janitrol hpt 18-60 thermostat. I want to replace it with a Robertshaw 9420 thermostat. However, I'm not sure about some of the wiring. I have 5 wires hooked to Janitrol as follows: Y terminal = yellow wire G terminal = green wire R terminal = red wire O terminal = white wire E terminal = blue wire C terminal = nothing hooked here E is jumpered to W2 with a copper wire The Robertshaw manual shows where the 5 wires go, but also lists a C terminal as 24 VAC, Transformer Common Side. Is there supposed to be something hooked to this terminal? And do I need to jumper anything? Hope someone can help me out here.
| | Replies:
|
| theduke03 | "Re(1):Replacing Janitrol hpt 18-60 thermostat" , posted Mon 16 Jun 21:42:  
That C terminal needs to be connected to common(C) in the air handler. If you have an extra wire you can connect it to C at both ends or get another stat, or pull an extra/new t-stat wire. W2 should be jumpered to E.
"My dad was the most feared furnace fighter in Northern Indiana."
[this message was edited by theduke03 on Mon 16 Jun 21:44] |
| | Houston204 
| "Re(2):Replacing Janitrol hpt 18-60 thermostat" , posted Tue 17 Jun 00:07  
I agree with Duke, C is required.
"Tip of the Day" Remember to remove power first.
|
|
|
|  |
|