were do the control wires that come from the outside coil go on a bryant 90i furnace and is there anything else that has to be done to the control board to make it work

 


Replies:

Houston204



98.196.66.53

"Re(1):a/c for bryant 90i" , posted Tue 17 Jun 21:11user profileedit/delete messagepost reply


The outdoor unit connects to Y and C if you have a single speed standard condenser outside.

Your control board must also be supplied with power and wired to a thermostat. It will probably also have jumpers that will need to be configured. After you start it you should measure your temperature rise across the unit and compare it to the nomenclature.