"Rheem Condenser fan won't come on after storm" , posted Fri 20 Jun 21:30user profileedit/delete messagepost reply


We have a Rheem RPKA-036JAS Heat Pump that was recently recharged, but following a violent storm, condenser fan will not come on. Unit hums and can feel heat from outside condenser unit. Have since turned unit off. Any advice will be greatly appreciated. Thank You.

 


Replies:

Jojo98

68.53.201.185

"Re(1):Rheem Condenser fan won't come on after" , posted Sat 21 Jun 00:16user profileedit/delete messagepost reply


Call a service company and have them replace the fan motor.

 

 

Houston204



98.196.66.53

"Re(2):Rheem Condenser fan won't come on after" , posted Sat 21 Jun 01:25:user profileedit/delete messagepost reply


If the fan spins freel when power is removed it is probably only your cap. Capacitor can hold a charge for a couple of minutes after removing power. Remove power, wait 2 minutes and short across the terminals and terminals to ground before handling.



Since it is a heatpump, it could also be the defrost control board.

"Tip of the Day" Remember to remove power first.