| lawnmower1 | "Media filters?" , posted Mon 23 Jun 14:40  
Greetings, This question is linked to another thread regarding my apparently low flowing return air and evaporator coil freeze up. The system was installed with a 20x25x5 media filter rated at 2000 cfm. Has anyone had experience with these high capacity filters? Before we attempt to enlarge the return duct (16") I would like to know if the filter might be too restrictive. The filter rack in the air handler unit uses a 20x22x1. A 5" pleated filter should have a lot more surface area and flow better, right? Thanks, ebc
| | Replies:
|
| yuri 
| "Re(1):Media filters?" , posted Mon 23 Jun 19:46:  
If you have the 20x25x5, that filter has a very large surface area and 2000 cfm is good for 5 tons of A/C. That is the largest standard filter available and should be no problem. I see them all the time and sell them. I would use a MERV 8 or 10 filter and stay away from the MERV 16 unless the ducts are larger. 1" dense/low micron filters can be a big problem as some furnaces and air handlers are not designed for that high a static pressure drop.
Yuri
[this message was edited by yuri on Mon 23 Jun 19:49] |
| | lawnmower1 | "Re(2):Media filters?" , posted Mon 23 Jun 20:43  
Thanks. I let the system run a few hours w/o the filter in place. The coil started freezing anyway. Looks like I need more return vent flow. Regards, ebc
|
|
|
|  |
|