PROBLEM WITH MY TRANE XE1000 CONDENSER FAN - http://www.hvacmechanic.com/ Forums


Original message

adonne1791

74.140.134.221

"PROBLEM WITH MY TRANE XE1000 CONDENSER FAN" , posted Thu 26 Jun 20:47user profileedit/delete messagepost reply


I Came home yesterday and the house was 88. I walked outside and the condenser fan was not moving and the motor was humming. I pushed on the blades with a stick and they started turning, but the wrong direction. My brother said I needed a new motor and purchased an A.O. smith universal motor. On my trane unit motor there was 3 wires. Brown, Black, and purple. On the new motor there are 4 wires. Brown, Brown/white trace, black and white. He could not figure out how to wire them... Also the new motor came with a cap. Can any one tell me how these should be wired together?

Andy Donnelly

 


Replies:

Houston204



98.196.66.53

"Re(1):PROBLEM WITH MY TRANE XE1000 CONDENSER " , posted Thu 26 Jun 22:21user profileedit/delete messagepost reply


If the old motor was connected to a dual capacitor, leave the old capacitor's Orange connected to H and red connected to C.
(only remove the 2 wires that went to the old motor)



Connect the new white to the contactor red point and black to the contactor black point. the 2 brown wires connect to opposite points on your new capacitor.

"Tip of the Day" Remember to remove power first.

 

 

adonne1791

74.140.134.221

"Re(2):PROBLEM WITH MY TRANE XE1000 CONDENSER" , posted Sun 29 Jun 10:37user profileedit/delete messagepost reply


Ok. I have the fan wired correctly. Thanks for that diagram. That was perfect. It seems to be moving alot of air and in the correct direction. But I have no cold air inside? Is there a reset for the compressor somewhere or has it burned out? How can I tell?

Andy Donnelly

 

 

Houston204



98.196.66.53

"Re(3):PROBLEM WITH MY TRANE XE1000 CONDENSER" , posted Sun 29 Jun 11:34user profileedit/delete messagepost reply


The compressor can be cooled with a water hose.(Remove power first)

If the old cap was a dual cap, you must leave it wired to C and Herm for the compressor to work. You would end up with 2 caps.