| rr man | "Wiring for Honeywell TH5220D1003, set on cool" , posted Thu 26 Jun 21:42  
I have a 2 1/2 ton Goodman self contained heat pump with a heat strip which was set up with a Janitrol HPT 18-60 thermostat. I replaced that with a Honeywell TH5220D1003 thermostat. The Janitrol was wired: Y= yellow G= green R= red O= white E= blue (also jumpered to W2) C=no wire
I wired up the new Honeywell: Y= yellow G= green R= red (also jumpered to Rc) O/B= white E = blue
I have the thermostat set on cool and the compressor runs, but it blows out heat instead of cool. Did I miswire it? Any suggestions will be greatly appreciated.
| | Replies:
|
| Houston204 
| "Re(1):Wiring for Honeywell TH5220D1003, set o" , posted Thu 26 Jun 22:30  
Place a jumper wire between Aux and E. Other than that, you have wired it correctly.
You must configure your new stat for heatpump operation. option 1 = 5 2 = 0
"Tip of the Day" Remember to remove power first.
|
| | rr man | "Re(2):Wiring for Honeywell TH5220D1003, set o" , posted Fri 27 Jun 09:11  
quote: Place a jumper wire between Aux and E. Other than that, you have wired it correctly. You must configure your new stat for heatpump operation.option 1 = 52 = 0
...
Thank you, thank you, thank you! I completely forgot to configure it for heatpump operation. You're a life saver!! It works like a charm now!!
|
|
|
|  |
|