"Wiring for Honeywell TH5220D1003, set on cool" , posted Thu 26 Jun 21:42user profileedit/delete messagepost reply


I have a 2 1/2 ton Goodman self contained heat pump with a heat strip which was set up with a Janitrol HPT 18-60 thermostat. I replaced that with a Honeywell TH5220D1003 thermostat. The Janitrol was wired:
Y= yellow
G= green
R= red
O= white
E= blue (also jumpered to W2)
C=no wire


I wired up the new Honeywell:
Y= yellow
G= green
R= red (also jumpered to Rc)
O/B= white
E = blue

I have the thermostat set on cool and the compressor runs, but it blows out heat instead of cool. Did I miswire it? Any suggestions will be greatly appreciated.

 


Replies:

Houston204



98.196.66.53

"Re(1):Wiring for Honeywell TH5220D1003, set o" , posted Thu 26 Jun 22:30user profileedit/delete messagepost reply


Place a jumper wire between Aux and E. Other than that, you have wired it correctly.

You must configure your new stat for heatpump operation.
option 1 = 5
2 = 0

"Tip of the Day" Remember to remove power first.

 

 

rr man

24.31.117.50

"Re(2):Wiring for Honeywell TH5220D1003, set o" , posted Fri 27 Jun 09:11user profileedit/delete messagepost reply


quote:
Place a jumper wire between Aux and E. Other than that, you have wired it correctly. You must configure your new stat for heatpump operation.option 1 = 52 = 0 ...
Thank you, thank you, thank you! I completely forgot to configure it for heatpump operation. You're a life saver!! It works like a charm now!!