"Question before I spend the money" , posted Fri 27 Jun 07:44user profileedit/delete messagepost reply


AC has been working fine for 5 years. Yesterday, it stopped blowing cold air. When we got home from work everything was working fine, it was at around 9:00 p.m. that we noticed the AC outside turn off. We thought it had reached the temperature and was shutting off. Well it never shut off, it just wasn't as loud as it had been. Now the outside unit is on but isn't loud as it's been. The fan turns, and I can feel air coming out. The air handler is on and working. I notice no condensation on anything. I've reset the breakers ... anyone have any ideas?

Thanks

Hot in here

 


Replies:

Houston204



98.196.66.53

"Re(1):Question before I spend the money" , posted Fri 27 Jun 08:26:user profileedit/delete messagepost reply


Dual capacitor outside has swollen and needs replacement.

It will probably resemble a beer can left in the freezer overnight.

Caps can hold a charge for a few minutes after removing power.

Be Safe.

"Tip of the Day" Remember to remove power first.