running heat all the time - http://www.hvacmechanic.com/ Forums


Original message

chesterkatie

24.191.135.36

"running heat all the time" , posted Sat 28 Jun 17:00user profileedit/delete messagepost reply


weil-mclain CGt-5-PIN series 1 CP4858496

I had the little box for the 3 way valve replaced on the top of the unit last year because it kept my boiler on and the heat going reguardless of what the thermostat said - it was about 90 degrees in my house. SO heat and boiler on at all times, no break from either.

Now the heat keeps running - not really the boiler. I have baseboard heating BTW. The boiler actually shuts off from time to time but the baseboards are still getting heat pumped through them. We disconnected the whole thermostat from the wall and no change. We finally just closed the valve that controls the heat to the baseboards. Heating guy cant figure it out. SO break from constantly running boiler, but heat keeps running throughout the house.

Any guesses? TIA

 


Replies:

theduke03

24.250.18.179

"Re(1):running heat all the time" , posted Sat 28 Jun 18:22user profileedit/delete messagepost reply


Your heating guy couldn't figure it out? Sounds like you need a new heating guy. Answer me this: Is the circulator running when problem occurs? That would suggest a miswired control. It could also be a zone valve stuck open or system installed without flow-checks. Did the heating guy use a meter?

"My dad was the most feared furnace fighter in Northern Indiana."

 

 

chesterkatie

24.191.135.36

"Re(2):running heat all the time" , posted Sat 28 Jun 22:12user profileedit/delete messagepost reply


No, he did not have a meter. My heating system does not have specific zones. Im rather surprised he didnt figure it out either. He wants to order a whole new 3 way box thingie and ill end up dropping another 400 bucks on it for a 1 year fix....

which is what brought me to this wonderful website....

i personally think there is a short somewhere in the wiring brought on by heat, condensation, etc whatever, that shorted it out becuase its fairly new... 4 years old new. too old for typical new appliance malfunctions, too young to die out. but he cannot figure out that short, to be honest i would be happier if he replaces the interior thermostat rather than me spend the bucks on another 3 way valve thing (which by the way finctions exactly how it says it should in its instructions.)

kate

 

 

theduke03

24.250.18.179

"Re(3):running heat all the time" , posted Sun 29 Jun 08:39user profileedit/delete messagepost reply


You really need a new heating guy. When the next guy arrives, don't let him in the house without a meter. If he says he doesn't have one then tell him to get off your property and call someone else.

"My dad was the most feared furnace fighter in Northern Indiana."

 

 

chesterkatie

24.191.135.36

"Re(4):running heat all the time" , posted Sun 29 Jun 11:32user profileedit/delete messagepost reply


Sorry, but i do have to ask, what would a meter be used for there?

kate

 

 

Houston204



98.196.66.53

"Re(5):running heat all the time" , posted Sun 29 Jun 12:13user profileedit/delete messagepost reply


To verify if the actuator has a demand to open or you have a sticking valve.

"Tip of the Day" Remember to remove power first.

 

 

chesterkatie

24.191.135.36

"Re(6):running heat all the time" , posted Sun 29 Jun 13:16user profileedit/delete messagepost reply


gotcha, thanks!

kate

 

 

Houston204



98.196.66.53

"Re(4):running heat all the time" , posted Sun 29 Jun 10:51user profileedit/delete messagepost reply


"Tip of the Day" Remember to remove power first.

 

 

theduke03

24.250.18.179

"Re(5):running heat all the time" , posted Sun 29 Jun 12:03:user profileedit/delete messagepost reply


Your dog looks a bit angry. What do you feed that thing?
I think what houston is saying is that this rabid wolf is a better service tech than your guy.

"My dad was the most feared furnace fighter in Northern Indiana."

[this message was edited by theduke03 on Sun 29 Jun 12:07]

 

 

Houston204



98.196.66.53

"Re(6):running heat all the time" , posted Sun 29 Jun 12:15:user profileedit/delete messagepost reply


Don't worry he won't bite, you just have to pet his head.

Have you ever heard that one before. I always counter with "Dogs don't bluff".

I just meant GRRR.

"Tip of the Day" Remember to remove power first.

[this message was edited by Houston204 on Sun 29 Jun 12:16]

 

 

theduke03

24.250.18.179

"Re(7):running heat all the time" , posted Sun 29 Jun 12:33user profileedit/delete messagepost reply


Only once. A customer had a German shepard that looked like the picture above. I asked them to put him in a room or a cage and they did. The thing that kills me is that once I went into the basement they let him loose. I was trapped and had to crack open the basement door to repeat my request for the dog to be penned up. That pissed me off. What a bunch of jamokes!