| kef | "Weathertron to Ritetemp 8085c thermostat" , posted Sun 29 Jun 20:54:  
Hi All,
I have purchased a Ritetemp 8085c thermostat to replace a Weathertron thermostat handling a Trane heatpump and furnace with emergency heat. Unfortunately the Ritetemp document is not detailed enough to account to all the wires that are connected to the old Weathertron thermostat.
So which wires go to which:
Weathertron BAYSTAT240A (old): Red wire = R Brown wire = T Orange wire = O Green wire = G Yellow wire = Y Black wire = X2 Blue wire = B White wire = W
Now where should these wires connect to on the 8085C?
Ritetemp 8085C C = H = W2 = RC = O = B = RH = W = Y = G = A =
Thanks in advance for your help. -Kef
[this message was edited by kef on Sun 29 Jun 21:03] | | Replies:
|
| Houston204 
| "Re(1):Weathertron to Ritetemp 8085c thermosta" , posted Sun 29 Jun 21:04  
C = blue W2 = white & Black Rc & Rh = red O = orange W & Y = yellow G = green tape off brown
behind the stat... jumper ELECT select PUMP
I don't think much of that stat. Honeywell, White Rodgers and Robertshaw are the brands that the pro's use.