Hi All,

I have purchased a Ritetemp 8085c thermostat to replace a Weathertron thermostat handling a Trane heatpump and furnace with emergency heat. Unfortunately the Ritetemp document is not detailed enough to account to all the wires that are connected to the old Weathertron thermostat.

So which wires go to which:

Weathertron BAYSTAT240A (old):
Red wire = R
Brown wire = T
Orange wire = O
Green wire = G
Yellow wire = Y
Black wire = X2
Blue wire = B
White wire = W

Now where should these wires connect to on the 8085C?

Ritetemp 8085C
C =
H =
W2 =
RC =
O =
B =
RH =
W =
Y =
G =
A =

Thanks in advance for your help.
-Kef

[this message was edited by kef on Sun 29 Jun 21:03]

 

Replies:

Houston204



98.196.66.53

"Re(1):Weathertron to Ritetemp 8085c thermosta" , posted Sun 29 Jun 21:04user profileedit/delete messagepost reply


C = blue
W2 = white & Black
Rc & Rh = red
O = orange
W & Y = yellow
G = green
tape off brown

behind the stat...
jumper ELECT
select PUMP



I don't think much of that stat. Honeywell, White Rodgers and Robertshaw are the brands that the pro's use.

"Tip of the Day" Remember to remove power first.