I am wiring a Honeywell T8011R.
The theromstat are G,C,R,W1,Y,L,W2,E,B,& O.
W1 and Y have a factory jumper.
The wires from the heatpup/ac unit are:
Green, Blue, White, Yellow, Red, Orange, & brown.
What wires go to which terminals?

Angusheeler

 


Replies:

Houston204



98.196.66.53

"Re(1):Honeywell T8011R" , posted Tue 1 Jul 22:13:user profileedit/delete messagepost reply


Color codes vary. Especially C (common) and E(emergency heat). Post the terminals that your wires are connected to at the fancoil.

Carrier usually uses brown for common. Trane usually uses blue for common(which they identify as B instead of C). I have also seen black used for common. If you wire Common incorrectly it will damage a fuse or transformer (many Rheem and Trane units do not have a low voltage fuse)

Most brands use O for the reversing valve, Rheem and Ruud use B for the revering valve. You won't use both O and B...


This is only an example and does not necessarilly represent your color codes. Common , E and your reversing valve wire must be identified.

"Tip of the Day" Remember to remove power first.