"Carrier 38CK Diagnosis" , posted Wed 2 Jul 20:29user profileedit/delete messagepost reply


I have a non-functioning Carrier 38CK compressor unit. Unit was working fine and has stopped functioning without any hints/ prior indications of an pending issue.

Neither the coolant compressor nor fan on the Carrier unit are running. Interior house blower fan runs fine.

I have a second 38CK unit that is operating without any issues.

Looking for suggestions on debugging/isolating the issue.

Thanks,

Getting Warm in Chicago!

 


Replies:

theduke03

24.250.18.179

"Re(1):Carrier 38CK Diagnosis" , posted Wed 2 Jul 21:16user profileedit/delete messagepost reply


I would start by checking the breaker to the outdoor unit. If it's tripped then reset it and report how many seconds it takes to trip again or whatever happens. Post results.

"My dad was the most feared furnace fighter in Northern Indiana."

 

 

Houston204



98.196.66.53

"Re(2):Carrier 38CK Diagnosis" , posted Wed 2 Jul 23:01user profileedit/delete messagepost reply


The dual capacitor in the condenser is probably swollen and needs replacement.

"Tip of the Day" Remember to remove power first.