weak/noair - http://www.hvacmechanic.com/ Forums


Original message

tallnok

74.195.244.63

"weak/noair" , posted Sat 5 Jul 12:50user profileedit/delete messagepost reply


my ac was just repaired a week or two ago(charged),the unit outside seems to be working although i noticed some frost on line.the indoor unit is running and the cage is spinning but little to no air is coming out of the vents. i also noticed some dripping in the crawl space underneath uniti cleaned filters,and tried to clean sq cage as best i could.what can i do?

 


Replies:

oldmangobles

64.85.145.187

"Re(1):weak/noair" , posted Sat 5 Jul 14:11user profileedit/delete messagepost reply


the indoor coil mat be iced up.can you turn on the furnace to melt ice on the coil inside?if so,defrost coil to get the air flow back,but if your coil is icing up it is probably still undercharged or the airflow is obstructed.call the service tech back in to finish the job.

old man mike

 

 

allen1980

72.65.150.176

"Re(2):weak/noair" , posted Sat 5 Jul 15:19user profileedit/delete messagepost reply


yes you will need to thaw the ice on the evap. coil.turn the thermostat to off and turn the fan from auto to the on position .untill the coil is thawed then check the coil it is probably dirty and needs to be cleaned.then you will need to have the freon checked because when the tech charged it before he probably over charged it.