"Bryant furnace/blower cycling problem with AC" , posted Mon 7 Jul 19:59:user profileedit/delete messagepost reply


I have a Bryant furnace and compressor. Every now and then the unit acts a bit funky. The unit will come on when it hits the temp set on the thermostat. The unit will run fine and then the blower will go off and on while the compressor stays running. The compressor will go off when it hits the desire temp . . but during that time the furnace/blower will go on and off several times.

sath

[this message was edited by sath2 on Tue 8 Jul 12:51]

 

Replies:

Houston204



98.196.66.53

"Re(1):Bryant furnace/blower cycling problem w" , posted Tue 8 Jul 23:59:user profileedit/delete messagepost reply


Do you own a meter?
First, measure your cap.
If the cap is okay, verify that voltage is present when your motor drops out.

Caps will hold a charge for 2 or 3 minutes after removing power, wait at least that long before handling it.

"Tip of the Day" Remember to remove power first.

[this message was edited by Houston204 on Wed 9 Jul 22:19]

 

 

sath2

209.31.135.126

"Re(2):Bryant furnace/blower cycling problem w" , posted Wed 9 Jul 08:52user profileedit/delete messagepost reply


We don't own a meter, but last year we had the same (intermittent) problem and our HVAC contractor used a meter and couldn't find anything wrong. They actually thought it might be the thermostat so they replaced it . . . but we still had the problem about a week later. Since I posted this, the system has worked fine, but I'd like to know why it does this from time-to-time.

sath