Carrier Model 58DXT - Blower Speed Adjust. - http://www.hvacmechanic.com/ Forums
| Original message
| Replies:
|
| theduke03 | "Re(1):Carrier Model 58DXT - Blower Speed Adj" , posted Mon 14 Jul 16:47  
Your problem is not the blower speed, which should not have been touched, or changed during stat replacement or re-installation of furnace. The problem is with the a/c system, could be several things, low charge, dirty condenser, or open/broken attic ducts. You can inspect any attic return ducts and hose out the coil on outdoor unit good. If coil is clean and ducts are intact and problem persists then it's most likely low on charge and you will need a pro.
"My dad was the most feared furnace fighter in Northern Indiana."
|
| | theduke03 | "Re(3):Carrier Model 58DXT - Blower Speed Adj" , posted Mon 14 Jul 17:18:  
The thermostat does not control the blower speed, that is accomplished by the circuitboard in the furnace. There is no way to do what you propose, and like I said, those speeds should not have been changed. It is possible that your indoor coil is freezing up and blocking airflow. If you don't believe me then open up the furnace and look at the circuitboard. If a black wire is on the COOL terminal then it's already on high speed. Have you checked your filter?
"My dad was the most feared furnace fighter in Northern Indiana."
[this message was edited by theduke03 on Mon 14 Jul 17:19] |
|
|
|  |
|