condenser not turning off or on properly - http://www.hvacmechanic.com/ Forums
Original message
| sainttammany | "condenser not turning off or on properly" , posted Mon 14 Jul 19:35  
Rheem classic X. Sometimes my compressor and exterior fan does not come on when it should. shutting everything down and restarting seems to cure this until it happens again, and sometimes it does not go off when it should freezing up the unit. Is there a relay for the condenser fan that could be causing the problems?
| | Replies:
|
| TnNATE1412 | "Re(1):condenser not turning off or on properl" , posted Mon 14 Jul 19:53  
Need to replace the contactor on the unit. Sounds like it is pitted and welding stuck at times and not making connection when it doesn't start running.
|
| | sainttammany | "Re(2):condenser not turning off or on properl" , posted Mon 14 Jul 19:56  
Thanks, a lot. U got an online source for the part?
|
| | Houston204 
| "Re(3):condenser not turning off or on properl" , posted Mon 14 Jul 23:19:  
http://arnoldservice.com/contactors.htm
I like the $22 2pole 40 amp contactor on the bottom of the list.
"Tip of the Day" Remember to remove power first.
[this message was edited by Houston204 on Mon 14 Jul 23:21] |
|
|
|  |
|