"condensation unit wont start!" , posted Thu 17 Jul 20:37user profileedit/delete messagepost reply


Hey guys, my capacitor on my condensing unit went, so I replaced it. I checked the contact to make sure it turns on correctly and it does. However, the thermostat will not turn the unit on and the blower is constantly on when I turn the breaker on regardless of the thermostat. Any help on what could possibly be the cause of this would be greatly appreciated. I have a trane unit and I think the last guy who replaced the blower motor may have rewired something incorrectly. It worked fine for about a year.

much appreciated!!

 


Replies:

Houston204



98.196.66.53

"Re(1):condensation unit wont start!" , posted Thu 17 Jul 21:40user profileedit/delete messagepost reply


Is this a gas or electric furnace?
Do you have 24 volts between R to C (C is probably labeled B) at your furnace?

"Tip of the Day" Remember to remove power first.

 

 

inneedofhelp

76.26.59.122

"Re(2):condensation unit wont start!" , posted Thu 17 Jul 22:01user profileedit/delete messagepost reply


It is electric. and yes I have 24V. I know the ltv use to have kind of like a 18 pin jack that use to go from the old motor to the ltv and pins 1 and 9 were orange and blue with the rest white I believe it had something to do with the fan control as far as the blower motor goes now it looks like a capacitor was added I have a red and a blue not connected to anything and black is to black and green is grounded and one more i dont remember the color whether its orange or yellow connected to a red. And the blower stays on constantly when the breaker is switched on. Now before I replaced the capacitor on the condensing unit which is all I did, the condensing unit came on (Trane xr12)Now it only turns on when the contact is pushed in manually.

much appreciated!!

 

 

Houston204



98.196.66.53

"Re(3):condensation unit wont start!" , posted Thu 17 Jul 22:50user profileedit/delete messagepost reply


Did you measure for 24 volts, or just assuming it.
Do you get 24 volts to the outdoor unit?
Is this a heat pump?

"Tip of the Day" Remember to remove power first.

 

 

inneedofhelp

76.26.59.122

"Re(4):condensation unit wont start!" , posted Sun 20 Jul 13:06user profileedit/delete messagepost reply


Sorry I was mistaken about the 24V. No I was not getting 24V at the condensing unit Nor was the transformer converting any Low Voltage the Input had the 208 and there was no output. Do I just need to replace the transformer or is there something else that may have also caused the transformer to go.
Thanks...

much appreciated!!