"heatpump problem" , posted Sun 20 Jul 22:00user profileedit/delete messagepost reply


ok last week I had extremly high head pressure on a 2 1/2 ton rheem heat pump (350 to 400). Coils were clean, drier clear so I replaced the txv. Pressures returned to normal 250 and 75. Now the unit will not get the temp in the house below 75 degrees during the hottest part of the day. The really odd part is when the head pressure was so high it cooled the house just fine. cycled on and off just fine and now it runs continuous from noon to dark and runs fine all night. This unit is slated to be replaced soon but I would like to know what is causing this.

Tim

 


Replies:

mississippi

67.142.130.23

"Re(1):heatpump problem" , posted Sun 20 Jul 22:10user profileedit/delete messagepost reply


may need to adjust txv if adjustable.

 

 

tim6820

70.149.244.45

"Re(2):heatpump problem" , posted Sun 20 Jul 22:14user profileedit/delete messagepost reply


txv has a bulb not adjustable as far as i can tell. I am a chilled water and chiller installer I know enough about split units to mess one up.

Tim

 

 

mississippi

67.142.130.23

"Re(3):heatpump problem" , posted Sun 20 Jul 22:19user profileedit/delete messagepost reply


whats your subcool temp. could be slightly low on freon

 

 

tim6820

70.149.244.45

"Re(4):heatpump problem" , posted Sun 20 Jul 22:27user profileedit/delete messagepost reply


ok subcooling is the differce in temp from the guage and the temp of the suction line right.

Tim

 

 

tim6820

70.149.244.45

"Re(5):heatpump problem" , posted Sun 20 Jul 22:36user profileedit/delete messagepost reply


I have tried adding a little freon to it but it just make the head pressure go up and the air temp at the unit seems to go down.

Tim

 

 

theduke03

24.250.18.179

"Re(6):heatpump problem" , posted Wed 23 Jul 19:36:user profileedit/delete messagepost reply


I think you should have washed the condenser reguardless of it's appearance, then measure your suction and liquid line temps as well as the outdoor ambient temp. Otherwise pressures are relatively meaningless. Subcooling is the difference between the liquid line temp and high side saturation temp(on gauge).
Same thing as a chiller.