Need help with baystat240 - http://www.hvacmechanic.com/ Forums
| Original message
| Replies:
|
| TnNATE1412 | "Re(1):Need help with baystat240" , posted Mon 21 Jul 20:31  
I would personally go for the Pro8000 (1008) model, since this is the contractor model. This model you can program off the wall, re-attach and let it run.
Some installers did not run seperate wires to the heater strips (X2 is emergency call and W is for standard call). They only used 1 wire and jumpered it like yours. You are right about the connections you listed. Tape off the T wire. Be sure to turn OFF power to the INDOOR unit (you could have more than 1 breaker/fuse connection) before starting the change.
|
| | shark57 | "Re(2):Need help with baystat240" , posted Wed 23 Jul 18:49  
Thank You for posting so quickly. The info you gave is very helpful. I dont have the new thermostat yet so just to make sure i understand....I will want to connect the white wire to the appropriate terminal for emergency heat and then jump it to the standard terminal just like the old one?
|
|
|
|  |
|