"27 vac from bad transformer?" , posted Wed 23 Jul 21:42user profileedit/delete messagepost reply


HELLO ALL, and thanks in advance for those who look and help. I have troubleshot my system till I am blue. Here's what is happening. The relay/contactor goes offline randomly. The old one blew apart so i have replaced the old contactor and have now feel it is the short cycle timer (SCT) that is kicking the contactor offline. I don't believe there is a high enough current draw from the compressor to cause the shut off. I do know that the tranformer is sending 27 VAC not 24 VAC, to the contactor and the SCT. Would this 3 volts be making havoc for the contactor/SCT. If I disconnect the timer, the unit runs w/o fail. With it plugged in the unit will come and go randomly. thanks again.

 


Replies:

mississippi

67.142.130.41

"Re(1):27 vac from bad transformer?" , posted Thu 24 Jul 12:36user profileedit/delete messagepost reply


27 volts not uncommon from transformer

 

learner

70.73.177.71

"Re(1):27 vac from bad transformer?" , posted Thu 24 Jul 08:38user profileedit/delete messagepost reply


Hi,
Then wouldn't it be the SCT a suspect? Higher voltage means not enough draw of current at the load side. Open or lower than normal load will show higher voltage

 

 

Freon

68.220.31.105

"Re(2):27 vac from bad transformer?" , posted Thu 24 Jul 16:03user profileedit/delete messagepost reply


"If I disconnect the timer, the unit runs w/o fail."

What does that tell you? Replace the timer... voltages are fine.