Original message

wvd

24.149.104.60

"Bryant Plus 90 with a HK42FZ011 control board" , posted Tue 29 Jul 10:29user profileedit/delete messagepost reply


I have a Bryant Plus 90 with a HK42FZ011 control board. The 3 amp fuse blows when the unit is in cool mode. Fuse does not blow when in fan mode or heat mode. I am also using a Honeywell programable thermostat. I closed the contactor on the outdoor AC unit and it started with no problems. Does the contol board require a 3A slow blow fuse? Any other thoughts would be appreciated.

thanks

 


Replies:

thechris333

216.212.153.88

"Re(1):Bryant Plus 90 with a HK42FZ011 control" , posted Fri 1 Aug 15:06user profileedit/delete messagepost reply


If the system is a heat pump check the low voltage wiring inside the condenser by taking the fan off. One of the wires may have rubbed up against the copper and shorted. Also the reversing valve coil can be drawing heavy amps and blowing the fuse. If it is an air conditioner and not a heat pump you simply have a short in the low voltage wiring somewhere.

chris

 

yuri



142.161.80.250

"Re(1):Bryant Plus 90 with a HK42FZ011 control" , posted Tue 29 Jul 17:52user profileedit/delete messagepost reply


Uses a 3 amp auto type only. Check the low voltage wiring to the out door unit. May have been hit by weedwhacker, chewed by rodents or the dog. Sounds like you got a short in it.

Yuri