External unit not working - http://www.hvacmechanic.com/ Forums


Original message

Chingy

68.97.7.18

"External unit not working" , posted Fri 1 Aug 21:17user profileedit/delete messagepost reply


Hello, I have a esternal unit that is not working, It makes noise but the fan does not turn. It is going to cost 6k to replace entire Heat/Air unit. I can not afford that. I have replace a few fans and thermos in my days and I was wondering if replacing the motor in the external unit would fix this prob.I Will post the info on unit. below. Thanks for any help in advance.

Serial-L980219652
MFRNO-Ag036GB2
Style-36 MCE-000095ZR
MIN Circ- 21.3

Thanks again,
Russell

 


Replies:

RAY B

71.242.176.87

"Re(1):External unit not working" , posted Sat 2 Aug 07:17user profileedit/delete messagepost reply


Hi, First Check voltage to contactor coil 24vac when calling for cooling, then check 240vac on both sides of contactor, is fan motorn really Hot to touch?, is contactor pulling in when calling for cooling?, is compressor running?

Ray

40 yr old HVAC equipment is a Joy Forever?

 

pbreazeale

69.34.145.144

"Re(1):External unit not working" , posted Sat 2 Aug 00:06user profileedit/delete messagepost reply


If you hear a buzzing noise, it's probably the 24 volt calling.... probably a bad capacitor, or contactor.

 

learner

70.73.177.71

"Re(1):External unit not working" , posted Fri 1 Aug 22:01user profileedit/delete messagepost reply


Hi,
First is to diagnose the symptom, not replacing things.
Like do you have a power to the unit? Is the control lead to the
unit showing proper voltage when colling is called for?, etc., etc.