"low suction high head press." , posted Sat 2 Aug 22:23user profileedit/delete messagepost reply


48lb suction 340lb head. Clean coils evap and cond. Indoor was iced up. sitting at max amps. 10 deg split, 80deg indoor temp. Any ideas

From sin city

 


Replies:

amech

68.251.97.57

"Re(1):low suction high head press." , posted Sun 3 Aug 08:31user profileedit/delete messagepost reply


Need more information, Superheat and subcooling, O/A Temp, R/A & D/A temps, Indoor termp, ETC. With 110-120 outdoor entering temp, head pressure not out of line. Restriction is likely your problem. May be in the drier or metering device. Dirty filter, blocked Return. Is your blower plugged or even running at desired speed.

 

mississippi

67.142.130.36

"Re(1):low suction high head press." , posted Sun 3 Aug 01:07user profileedit/delete messagepost reply


restricted piston or txv or piston to small

 

Jojo98

69.246.153.58

"Re(1):low suction high head press." , posted Sat 2 Aug 22:33user profileedit/delete messagepost reply


Low on charge with that kind of head press?

 

pbreazeale

69.34.145.144

"Re(1):low suction high head press." , posted Sat 2 Aug 22:25user profileedit/delete messagepost reply


Low freon.

 

 

Hotshot

207.200.116.67

"Re(2):low suction high head press." , posted Sat 2 Aug 22:33:user profileedit/delete messagepost reply


No room for more gas, Compress amps at max plus 5%

From sin city

[this message was edited by Hotshot on Sat 2 Aug 22:41]

 

 

Freon

70.157.187.246

"Re(3):low suction high head press." , posted Sun 3 Aug 13:10user profileedit/delete messagepost reply


Please post some history... age?, new problem? Any work done where system was opened? Make/model.

It would appear the evap coil is starved so you'd expect high superheat. If there was a restriction then also high subcooling. Check the lineset for any damage from other people working around.