"Installed new T-stat & AC won't come on" , posted Sun 10 Aug 08:39user profileedit/delete messagepost reply


I had an old carrier heat pump t-stat and tried to change it out to a aprilaire 8346 digital. I did this on my downstairs unit and everything is fine. Upstairs, I changed them and now the system will not turn on, I even put the old one back on and it will not run. I did not cut off any power or breakers, is there a fuse I could have tripped? The wires are c (put brown wire here),,w2,r,g,y,o..same as old t-stat. Help! I have no ac

 


Replies:

amech

68.249.96.147

"Re(1):Installed new T-stat & AC won't come on" , posted Sun 10 Aug 08:57user profileedit/delete messagepost reply


Inside the indoor unit there should be a 3 or 5 amp mini fuse on the control board. If no fuse check for breaker on the transformer. A meter will also verify that you have main votage or secondary 24v at transformer to make sure it's not bad.

Hope this helps.

 

 

Houston204



98.196.66.53

"Re(2):Installed new T-stat & AC won't come on" , posted Sun 10 Aug 10:21user profileedit/delete messagepost reply


The indoor unit has 240 volts present, so turn off the disconnect(s) or breaker(s) before opening the panel.
(Probably not the breaker labeled heatpump, possibly AHU , Furnace, or Fancoil)

I don't have a Carrier example, but this is an example.

"Tip of the Day" Remember to remove power first.