I have two side by side condensers, one blows hot air (normal) and the other blows cold air. Is this a problem waiting to happen? I've read that dirty condenser coils impact the efficiency... any recommendations on a good cleaner/procedure?

 


Replies:

envirosystemtec

74.47.220.101

"Re(1):condensor question" , posted Sat 16 Aug 11:52user profileedit/delete messagepost reply


could be low on freon pull top off of condensor feel the compressor if hot its off on overload check the pressures if low charged then do a leak check check the filter inside if you have a high head pressure then may be you coil is dirty run water though the coil or you compressor isnt running maybe you have a bad capacitor seen duel caps blown up and still let the condensor fan run check those it has to be one

tim

 

Jojo98

68.60.207.210

"Re(1):condensor question" , posted Fri 15 Aug 23:13user profileedit/delete messagepost reply


Sounds like one of the compressors is not running. Flip the breaker off then on and see if the cold air condenser warms up. If not call a service company.