frosted suction line,low side 45,head is 275,outdoor temp 80,good airflow,clean filter,suction line temp 44,liquid line temp 80,70 degree air from supply vents. r-22 030 17 year old split sys.any ideas would be appreciated
| | Replies:
|
| envirosystemtec | "Re(1):frosted suction line" , posted Sun 17 Aug 22:36  
restriction put hand across evap coil feel bottom then top if their is a difference in temp either restricted metering devise or coil
tim
|
| Jojo98 | "Re(1):frosted suction line" , posted Sun 17 Aug 02:10  
Recheck your temps. Suct. wont freeze at 44deg. What is the superheat? Sounds like a restriction. Check for a temp. drop across the liquid line drier.
|
|
|
|