Blower Pulses On and Off Every Two Seconds - http://www.hvacmechanic.com/ Forums


Original message

FSUDAL

65.186.81.121

"Blower Pulses On and Off Every Two Seconds" , posted Tue 26 Aug 21:11user profileedit/delete messagepost reply


What could cause the blower fan on my residential Bryant Central Heating and Cooling unit to pulsate on and off every two seconds? If I shut off the system the fan seems to operate properly for a while but then unannounced the fault will occur again. Thanking you in advance for your help.

x

 


Replies:

fluepipe3

12.210.133.127

"Blower pulses on" , posted Wed 27 Aug 19:28user profileedit/delete messagepost reply


The fan blower capacitor is usually located on the side of the squirrel cage. First shut power off to furnace. Then look for a "tin can" silver attached to the squirrel cage. It will usually have 2 wires attached to it. Make sure the wires were pushed down all the way and not loose.( use insulated pliers, as cap can still hold a charge). If the were, unhook cap fron wires and unscrew cap from cap holder. Is it buldging or deformed? if so replace with one of the same valve. If you have access to capacitor checker you can test it, if not just replace it and see if that fixes the problem, they aren't expensive.

 

 

FSUDAL

170.135.241.45

"Re(1):Blower pulses on" , posted Fri 29 Aug 09:16user profileedit/delete messagepost reply


Thank you for your reply. I will take a peek over the weekend to inspect the part.

Ironically, I switched the fan setting on the programable thermostat upstairs from AUTO to ON (this causes the fan to run continuously on the low setting and then kick on high during cooling). The unit has been running fine ever since.

I wonder if the thermostat could potentially be the problem or if it may just be masking the capacitor problem since the blower does not need to start from a dead stop?

x

 

Jojo98

68.60.207.210

"Re(1):Blower Pulses On and Off Every Two Seco" , posted Tue 26 Aug 22:18user profileedit/delete messagepost reply


Sounds like a run capacitor.

 

 

FSUDAL

170.135.241.45

"Re(2):Blower Pulses On and Off Every Two Seco" , posted Wed 27 Aug 09:10user profileedit/delete messagepost reply


Thank you for your timely response. Although I was an electroncis tech in the USMC many years ago I am not an HVAC tech. How can I check to see if this is the problem and fix it?

I forgot to mention in my original post that the amber light is on and does not blink. I think this means no error code is currently being reported?

Also, are there any good resorces/books for someone like me to tap into--with pictures? :)

x

 

 

fluepipe3

12.210.133.127

"Blower pulses on" , posted Wed 27 Aug 19:30user profileedit/delete messagepost reply


What is the make and model number of your unit?

 

 

FSUDAL

170.135.241.45

"Re(1):Blower pulses on" , posted Fri 29 Aug 09:11user profileedit/delete messagepost reply


It is a Bryant 90i which cools and heats. I'm not sure if that is the actual model number or not. Let me know if that helps. Thanks again for sharing your knowledge!

x

 

 

fluepipe3

12.210.133.127

"picture" , posted Fri 29 Aug 21:51user profileedit/delete messagepost reply


www.basingerph.com/images/90imaintenance.pdf

 

 

FSUDAL

65.186.81.121

"Re(1):picture" , posted Sun 31 Aug 12:01user profileedit/delete messagepost reply


quote:
http://www1.snapfish.com/slideshow/AlbumID=245833489/PictureID=5687705966/a=143047178_143047178/t_=143047178 ...
Nice! Thank you for that. I looked around but could not find the run capacitor. I tried to attach two pictures in hopes that you help me find it (not sure it the pictures will come up for you. It doesn't seem like there is an easy way to share pictures on this site). The wires would suggest that it may be inside the motor?

Also, I switched the fan setting on the programmable thermostat upstairs from AUTO to ON (this causes the fan to run continuously on the low setting and then kick on high during cooling). The unit has been running fine ever since. I wonder if the thermostat could potentially be the problem or if it may just be masking the capacitor problem since the blower does not need to start from a dead stop?

Thanks again!

Two pics via link;

http://www1.snapfish.com/slideshow/AlbumID=245833489/PictureID=5687705966/a=143047178_143047178/t_=143047178