| Paladin | "Thermostat Honeywell t8400c to Hunter 44360" , posted Wed 27 Aug 01:44  
Hi everyone,
I hope this is an easy fix
I followed the manual with the Hunter 44360 and used the labels to match the Honeywell t8400c wire markers over to the Hunter fan unit.
I get it all hooked up and at first it looked good, the AC started up. Later I find out it doesn't want to shut off, no matter what I set the temp to. By taking the unit off the base the AC did shut off, but I know the wiring has to be the issue. I have found manuals for both units, but I am not an electronics guy.
So what I need is someone to say Honeywell W wire goes to BLAH Hunter connector and so on. I am hooking up a 4 wire unit, I have R W G Y connectors in use on the Honeywell and this is to a Heat pump. I have set the hunter to be using the heat pump mode.
Thanks for any help
Ron
| | Replies:
|
| TnNATE1412 | "Re(1):Thermostat Honeywell t8400c to Hunter 4" , posted Wed 27 Aug 06:35  
First, if you are only using 4 wires....you DON'T have a heat pump. 1. R to Red 2. W to W 3. Y to Y 4. G to G
If you have 4 wires, you have a heating/air only. Set the thermostat to CONVENTIONAL.
|
| | Paladin | "Re(2):Thermostat Honeywell t8400c to Hunter 4" , posted Wed 27 Aug 22:14  
Yes, I found out today that the manual is misleading in that it says to change it from standard to heat pump if you have a heat pump. All is well for now (haven't tried heating yet).
Thanks everyone.
Ron
|
|
|
|  |
|