"replace air handler" , posted Wed 27 Aug 08:57user profileedit/delete messagepost reply


I WOULD LIKE SOME PROFESSIONAL ADVISE.MY HOUSE IS 1375 SQ FEET HEATED.THE AIR HANDLER LEAK INTO THE SECONDARY PAN DUE TO AGE.THE UNIT IS A TRANE 3 TON 10 SEER HEATPUMP.I CALLED A CONTRACTOR FOR HIS OPION.HE TOLD ME A 2.5 TON 13 SEER AIR HANDLER SHOULD WORK IF CHANGED.I WOULD APPRECIATE SOME IMPUTS. THANKS,

 


Replies:

dac122

205.232.0.60

"Re(1):replace air handler" , posted Tue 2 Sep 13:52user profileedit/delete messagepost reply


Yes, did the contractor inspect the system and determine why it was leaking? A clogged drain can be easily rectified, even by DIYers. A rusted out drain pan is a different story.

 

theduke03

68.9.234.3

"Re(1):replace air handler" , posted Wed 27 Aug 16:53user profileedit/delete messagepost reply


I would not replace a 3 ton air handler with a 2.5 ton air handler unless you're planning on replacing the heatpump too (with a 2.5 ton unit). Age does not cause leaks. Your water leak is most likely from a clogged drain or drain pan, or a rotted drain pan.

"My dad was the most feared furnace fighter in Northern Indiana."