"Coleman DGAT070BDE intermit. ign. fail" , posted Thu 28 Aug 23:32user profileedit/delete messagepost reply


Got a 10 year old coleman mobile home furnace that intermittantly drops power to the gas valve as soon as the blower is given 120v from the circuit board. Thought that maybe the amp draw from the blower was robbing power from the transformer and causing the gas valve to drop out; but 24v stays present at the transformer even as the blower starts. Tried unplugging blower but problem still occured as 120v was switched to blower. Tried new circuit board, checked all electrical connections... anybody see this?

 


Replies:

footprints

65.75.233.23

"Re(1):Coleman DGAT070BDE intermit. ign. fail" , posted Fri 29 Aug 17:30user profileedit/delete messagepost reply


Hey, I'm just a home owner, but I had a similar problem and the hvac guys kept changing the ignitor, which seemed to work until they left. Try replacing the pressure switch. Mine has worked ever since...

Todd

Todd

 

 

HVACRider



76.121.189.6

"Re(2):Coleman DGAT070BDE intermit. ign. fail" , posted Fri 29 Aug 20:07user profileedit/delete messagepost reply


Thanks for the suggestion; this furnace has a centrifugal switch on the booster fan motor in place of a pressure switch.

 

 

MechAcc

75.204.232.229

"Re(3):Coleman DGAT070BDE intermit. ign. fail" , posted Sat 30 Aug 15:26:user profileedit/delete messagepost reply


Sounds more like a control board problem.