| TnNATE1412 | "Re(1):Charging system by superheat/subcooling" , posted Tue 2 Sep 06:31  
Yes, you did it right. Keep up the good work and do it RIGHT every time! The indoor WB is used to figure the proper Superheat required. In order to figure required superheat, you need the Outdoor Ambient entering the coil, Return air ambient and Return air Wet Bulb Temp. Normally, if you have a TXV coil, you would charge by subcooling. Some systems, Rheem, Ruud, etc., still use Superheat for their charging whether you have a TXV or not. You have to look at each individual system and follow their directions for charging. Not all systems use the same subcooling values either. Check out the HVAC News.com for more info.
|
|
|
|  |
|