I'm replacing a thermostat with the subject thermostat however the old unit has a white wire that I can't map to the Honeywell unit. My AC/Heat Pump is a goodman with aux heat. Any Idea where the white wire goes. Also, are there any settings on the Honeywell that I need to set.
Thanks

Thanks Mike Perrotto

 


Replies:

mikep-sc

66.56.188.195

"Re(1):Honeywell TH3210D1004" , posted Sun 7 Sep 12:19user profileedit/delete messagepost reply


I forgot to mention that the old GE Thermostat has the following wires connected.
Yellow to Yellow, Red to Red, Green to Green and White to White (however there is not white terminal on the Honeywell TH3210D1004.
Thanks

Thanks Mike Perrotto

 

 

Houston204



98.196.66.53

"Re(2):Honeywell TH3210D1004" , posted Sun 7 Sep 15:05user profileedit/delete messagepost reply


Product Application
This thermostat provides electronic control of 24 VAC heat pump systems with auxiliary
heat (2 heat/1 cool).

If you are only using 4 conductors, you do not have a heatpump and need a different stat.

Color codes vary, use your old color/terminal combination not this example.

"Tip of the Day" Remember to remove power first.

 

 

mikep-sc

64.138.205.25

"Re(3):Honeywell TH3210D1004" , posted Mon 8 Sep 09:12user profileedit/delete messagepost reply


We checked the unit outside and it is a Goodman CKL 36-10.

Thanks Mike Perrotto

 

 

Houston204



98.196.66.53

"Re(4):Honeywell TH3210D1004" , posted Mon 8 Sep 19:55user profileedit/delete messagepost reply


That does not appear to be a heatpump.

"Tip of the Day" Remember to remove power first.

 

 

mikep-sc

64.138.205.25

"Re(5):Honeywell TH3210D1004" , posted Mon 8 Sep 20:32user profileedit/delete messagepost reply


Houston204
You're right this is not a heat pump. The Goodman unit is for Air,conditioning and there is an electric furnace (or heat coils) inside the air handler unit. Based on a process of elimination, I assume the White wire, coupled with the Red (power) wire, activates some relay that turns on the electric furnace when the Thermostat is on the heat setting/mode. The other wires activate the blower and the AC unit.

Thanks Mike Perrotto

 

 

Houston204



98.196.66.53

"Re(6):Honeywell TH3210D1004" , posted Mon 8 Sep 20:57user profileedit/delete messagepost reply


R = 24 volt power
G = fan
W = heat
Y = compressor

A heatpump stat will energize Y on demand for heat and cool.
You need a different stat.

"Tip of the Day" Remember to remove power first.

 

 

mikep-sc

64.138.205.25

"Re(7):Honeywell TH3210D1004" , posted Mon 8 Sep 21:09user profileedit/delete messagepost reply


ok thanks. Any thermostat recommendation for this installation?

Thanks Mike Perrotto

 

 

Houston204



98.196.66.53

"Re(8):Honeywell TH3210D1004" , posted Mon 8 Sep 23:07user profileedit/delete messagepost reply


A Honeywell RTH6300 is a good choice.



I use a Honeywell Visionpro touchscreen stat.

"Tip of the Day" Remember to remove power first.

 

 

mikep-sc

64.138.205.25

"Re(3):Honeywell TH3210D1004" , posted Sun 7 Sep 20:22user profileedit/delete messagepost reply


Houston204,

Thanks for your response.
You've bailed me out of several HVAC situations before and I respect your opinion.

This is a heat pump installation in my Daughters double wide mobile home. Tomorrow when it’s light out, we’ll get the exact model of the heat pump and post a reply here.

In the mean time, I hooked up the Honeywell TH3210D1004 thermostat as follows:
Yellow to Yellow
Red to Red
Green to Green
White to Aux

The Air Conditioner has worked well all day; however I haven’t had a chance to check if it works in heat mode.

I’ll get back to you with the heat pump’s model number.
Thanks

Thanks Mike Perrotto