Here are the facts:
1) No conductivity in
a) thermostat
b) secondary on transformer -installed a new one, smoked.
2) Condenser - spins when I press in the contactor.
3) Tested all wiring from transformer / relay / stat / board. All show near 0 resistance.
4) I opened the relay today, set my multimeter to ohms and rx1, and placed both prongs on the coil. The multimeter did not budge from infinity. Does that mean it's shorted?

How do I test the contactor coil? What else could it be?

Goodman 1826-1
http://www.flickr.com/photos/28565984@N07/2836698508/
http://www.flickr.com/photos/28565984@N07/2836796430/sizes/l/

 


Replies:

Jojo98

68.60.207.210

"Re(1):a/c dead" , posted Tue 9 Sep 23:01user profileedit/delete messagepost reply


A coil read with an ohm meter should read very little resistance at all, and the meter shouldn't count down from infinity. If it's an inexpensive relay, replace and see what happens.

 

ampulman

76.98.216.149

"Re(1):a/c dead" , posted Tue 9 Sep 17:23user profileedit/delete messagepost reply


When you touch the two test prods together, what does the meter read?

AM

 

 

tempacc

72.205.52.98

"Re(2):a/c dead" , posted Tue 9 Sep 17:31user profileedit/delete messagepost reply


It starts on infinity and moves to zero.

 

 

learner

70.73.177.71

"Re(3):a/c dead" , posted Wed 10 Sep 02:12user profileedit/delete messagepost reply


Hi,
Which relay did you open? Sounds like your meter was across a capacitor of sort. I'd trouble shoot why xformer smoked. Sounds like something on the secondary(24V AC) load side is dead shorted. Remove power and do a static trouble-shooting.

 

 

beginner

96.232.19.123

"Re(4):a/c dead" , posted Wed 10 Sep 17:49user profileedit/delete messagepost reply


"b) secondary on transformer -installed a new one, smoked."
Get yourself an inline fuse. Check where the short is. Common cultprit is the control wires to the contactor outside.

"4) I opened the relay today, set my multimeter to ohms and rx1, and placed both prongs on the coil. The multimeter did not budge from infinity. Does that mean it's shorted?"
No, it is not shorted. The coil is opened.

"How do I test the contactor coil? What else could it be?"
First remove power!!! You should get close to zero ohm or couple ohms across the coil. This is your internal resistance of the coil. If it measured infinite, the coil is opened. Get a new one.