Original message

gator8

65.33.238.133

"digital thermostat problem" , posted Tue 9 Sep 21:49user profileedit/delete messagepost reply


I just installed a ritetemp 6025, and now my ac runs continuously. Troubleshooting over the phone with ritetemp. they had me disconnect b from c, and r from rh. the compressor still ran. had me remove the #7 jumper. still ran. thay said this was not possable. after i hung up, i could smell that the heater was running. can my heat and ac run at the same time???

 


Replies:

theduke03

68.9.234.3

"Re(1):digital thermostat problem" , posted Tue 9 Sep 21:56user profileedit/delete messagepost reply


Did the system work ok before you changed stat? If so it's probably miswired. Hopefully you wrote down the original wiring configuration. If so then post it here for example:
Y=yellow
G=green
etc
etc.
What type of heat do you have?

"My dad was the most feared furnace fighter in Northern Indiana."

 

 

gator8

65.33.238.133

"Re(2):digital thermostat problem" , posted Tue 9 Sep 23:00user profileedit/delete messagepost reply


the system did work, just upgrading. my old wiring
blk = X2
org = O
grn = G
ylw = Y
brn = T
rd = R
wht = W jumped U
Bl = B

I wired it
blk = not used
org = O
grn = G
ylw = Y
brn = not used
rd = RH
wht = W2
bl = C

This is a trane XE 1000 w/ american standard heater bay96x1405

 

 

theduke03

68.9.234.3

"Re(3):digital thermostat problem" , posted Wed 10 Sep 20:39:user profileedit/delete messagepost reply


Well it looks like it's wired properly. Are your configuration jumpers set correctly for a heat pump system with auxillary heat as shown on page 20?

"My dad was the most feared furnace fighter in Northern Indiana."

[this message was edited by theduke03 on Wed 10 Sep 20:48]