I just installed a ritetemp 6025, and now my ac runs continuously. Troubleshooting over the phone with ritetemp. they had me disconnect b from c, and r from rh. the compressor still ran. had me remove the #7 jumper. still ran. thay said this was not possable. after i hung up, i could smell that the heater was running. can my heat and ac run at the same time???
| | Replies:
|
| theduke03 | "Re(1):digital thermostat problem" , posted Tue 9 Sep 21:56  
Did the system work ok before you changed stat? If so it's probably miswired. Hopefully you wrote down the original wiring configuration. If so then post it here for example: Y=yellow G=green etc etc. What type of heat do you have?
"My dad was the most feared furnace fighter in Northern Indiana."
|
| | gator8 | "Re(2):digital thermostat problem" , posted Tue 9 Sep 23:00  
the system did work, just upgrading. my old wiring blk = X2 org = O grn = G ylw = Y brn = T rd = R wht = W jumped U Bl = B
I wired it blk = not used org = O grn = G ylw = Y brn = not used rd = RH wht = W2 bl = C
This is a trane XE 1000 w/ american standard heater bay96x1405
|
| | theduke03 | "Re(3):digital thermostat problem" , posted Wed 10 Sep 20:39:  
Well it looks like it's wired properly. Are your configuration jumpers set correctly for a heat pump system with auxillary heat as shown on page 20?
"My dad was the most feared furnace fighter in Northern Indiana."
[this message was edited by theduke03 on Wed 10 Sep 20:48] |
|
|
|  |
|