wiring new compressor contactor - http://www.hvacmechanic.com/ Forums


Original message

Joe0205

68.54.162.253

"wiring new compressor contactor" , posted Wed 10 Sep 07:47user profileedit/delete messagepost reply


Hi, thank you for looking at my post. My old contactor has 2 sets of 2 posts on one side (see picture http://www.arnoldservice.com/burnt%20contactor.jpg ) and my new contactor has 2 posts on opposite sides of the contactor (see picture http://images.grainger.com/images/products/5B133.JPG ). My question, refering to the first picture, is where will the light blue and yellow wires will go on the new contactor. Thank you for your time.

 


Replies:

timdecker

64.31.225.128

"Re(1):wiring new compressor contactor" , posted Thu 11 Sep 15:24user profileedit/delete messagepost reply


The blue and yellow wires are for your 24 V supply voltage which will close the contactors when energized. They go on the two smaller side pins on the left side of your photo.

Greetings from Houston TX the AC capitol of the world!

 

 

Joe0205

68.54.162.253

"Re(2):wiring new compressor contactor" , posted Fri 12 Sep 09:53user profileedit/delete messagepost reply


Thanks! It is working fine now. Stay safe and I hope Ike spares you!

 

acefurnacefxr



70.226.6.113

"Re(1):wiring new compressor contactor" , posted Wed 10 Sep 08:47user profileedit/delete messagepost reply


They go on the coil, if you dont know what or were the coil is then you shouldent be messing with it to begin with

HVAC REPAIR IS NOT A DIY WEEKEND PRODJECT

I have been performing HVAC repairs for 23 years

http://www.barackobama.com

 

 

Joe0205

68.54.162.253

"Re(2):wiring new compressor contactor" , posted Fri 12 Sep 10:03:user profileedit/delete messagepost reply


...curmudgeons for Obama!

[this message was edited by Joe0205 on Fri 12 Sep 10:05]