i came accross a problem with a hunter fireplace model#hfs40-3, the burner fires when i turn the gas valve to the on position even if the t-stat is not calling for heat. im looking for some pointers.... thank you
Ryan Gamache
| | Replies:
|
| yuri 
| "Re(1):Hunter Fireplace Problem" , posted Sun 21 Sep 13:25:  
Short in the thermostat wires. 2 of them are touching each other. Check by the burner, may have got overheated/melted together. Disconnect one on the gas valve and see if it closes. VERY rare that the valve will be faulty/stuck open. Don't remove the one from the pilot generator or the pilot and everything will drop out.
Yuri
[this message was edited by yuri on Sun 21 Sep 13:27] |
| | gamacher | "Re(2):Hunter Fireplace Problem" , posted Sun 21 Sep 13:43  
i removed the thermostat completely off the wall and disconected the wires and still the same problem,
Ryan Gamache
|
| | learner | "Re(3):Hunter Fireplace Problem" , posted Sun 21 Sep 20:04  
Hi, If you suspect shorted wire, how about removing wires at the other end(FP end). Or gas valve might be stuck open.
|
| | yuri 
| "Re(3):Hunter Fireplace Problem" , posted Sun 21 Sep 18:33  
Remove one at the gas valve. Follow the wires from there and look for damage.