"Copper tubing size." , posted Mon 22 Sep 13:05user profileedit/delete messagepost reply


I'm about to have a new AC unit hooked up to my house. It's a
3 1/2 ton 14 sear R410 Rheem. The contractor said it should use a 1 1/8 copper line. Mine is 7/8. Now he's saying the 7/8 will be fine. Any adivce on what it should be?

 


Replies:

acefurnacefxr



12.70.121.2

"Re(1):Copper tubing size." , posted Mon 22 Sep 20:32user profileedit/delete messagepost reply


7/8 3/8 will be fine............u dont need 1 1/8 until u get to 5 ton, and even then on a short run 7/8 will work.

HVAC REPAIR IS NOT A DIY WEEKEND PRODJECT

I have been performing HVAC repairs for 23 years

http://www.barackobama.com

 

Lou Lopasco



24.59.8.13

"Re(1):Copper tubing size." , posted Mon 22 Sep 18:50user profileedit/delete messagepost reply


That depends...how long will the line set end up being?

*Rookie HVAC service and installations. 3 years on the force!*

 

 

sormi

70.114.145.150

"Re(2):Copper tubing size." , posted Mon 22 Sep 19:26user profileedit/delete messagepost reply


About 12 feet.

 

 

aircooled



99.147.86.86

"Re(3):Copper tubing size." , posted Tue 23 Sep 08:52user profileedit/delete messagepost reply


12 ft. of copper manufactures state line set min.15ft or flood back can be present.

I would add to line set, 7/8" is fine.