"Help with Blower Fan" , posted Mon 22 Sep 17:27user profileedit/delete messagepost reply


I am having issues with the Blower Fan in my Goodman Packaged Unit. The fan will not kick on after the unit starts its cooling cycle. Unit will then freeze up. I will shut down allow it to unthaw and start it back up and it will run fine for a few days then do it again. It has been going on for about 2 weeks now. Filter is clean and the Coils were combed and cleaned on 09/18/08. I removed the blower motor and had it tested, all tested fine. Please help!!

Dagreen

 


Replies:

TnNATE1412

24.158.140.10

"Re(1):Help with Blower Fan" , posted Mon 22 Sep 21:41user profileedit/delete messagepost reply


The blower time delay relay is failing. It needs to be replaced, or install a standard relay for the blower operation.

 

Lou Lopasco



24.59.8.13

"Re(1):Help with Blower Fan" , posted Mon 22 Sep 18:43user profileedit/delete messagepost reply


Well, if you had the motor tested for open windings, short to ground and the thing runs sporatically then I would think this is a circuit board or relay issue.

*Rookie HVAC service and installations. 3 years on the force!*

 

 

dagreen

75.250.61.85

"Re(2):Help with Blower Fan" , posted Mon 22 Sep 22:13user profileedit/delete messagepost reply


Thanks, I will try the relays first and go from there.

 

 

dagreen

70.221.162.190

"Re(3):Help with Blower Fan" , posted Mon 29 Sep 21:42user profileedit/delete messagepost reply


Replaced the relay, all seems to be working great. Thanks for the help!!