"Concord 80 plus oil furnace" , posted Sun 5 Oct 09:21user profileedit/delete messagepost reply


How long should a cycle be for this unit.
I have timed the cycle to be as follows:
unit fires up
2 minutes later blower kicks on and runs for 7 minutes.
unit shuts down for 9 minutes then fires up again for new cycle.
I am heating 4888 sq. ft.
Is this normal cycling or is this a short cycle?
the system seems to shut off before heat reaches 2nd floor.
I have a Honeywell round digital thermostat.
this is a brand new furnace.

thank you for your responce
Roger @ ClicktoRemodel

 


Replies:

amech

68.249.110.53

"Re(1):Concord 80 plus oil furnace" , posted Sun 5 Oct 09:42user profileedit/delete messagepost reply


Is your thermostat located next to a door, lamp, computer, window, outside wall, etc. If no false sources of heat, check limits or call out the installer.

 

 

clicktoreomdel

71.10.224.146

"Re(2):Concord 80 plus oil furnace" , posted Sun 5 Oct 15:16user profileedit/delete messagepost reply


tstat is on interior wall in common hall on 1st floor
(only 1 zone) not near any exterior door,lamp,window or heat source.
I turned the tstat up 1 degree and it cycles fine (longer)
but in order to maintain consistant temp, the cycles are way shorter.
is it possible the tstat is too sensitive?

thank you for your responce
Roger @ ClicktoRemodel

 

 

tom446



66.66.203.58

"Re(2):Concord 80 plus oil furnace" , posted Sun 5 Oct 11:21user profileedit/delete messagepost reply


Sounds like it may be tripping the limit. Start by making sure your filter is clean. Dirty evaporator coil or cracked heat exchangers are other causes. Also make sure all your returns and registers are open.

If in doubt call a pro !

 

 

clicktoreomdel

71.10.224.146

"Re(3):Concord 80 plus oil furnace" , posted Sun 5 Oct 15:26user profileedit/delete messagepost reply


had it cleaned and seasonal service 1 week ago, new filter, all registers are fully open.
return is centrally located in common hall on 1st floor.
no return in each room.

thank you for your responce
Roger @ ClicktoRemodel

 

 

yuri



142.161.109.112

"Re(3):Concord 80 plus oil furnace" , posted Sun 5 Oct 12:33user profileedit/delete messagepost reply


Check the owners manual for the tstat. Most of them have a cycles per hour adjustment. Set it for oil or hot water heating if you want longer cycles. The default is usually high efficiency gas unit.

Yuri

 

 

clicktoreomdel

71.10.224.146

"Re(4):Concord 80 plus oil furnace" , posted Sun 5 Oct 15:28user profileedit/delete messagepost reply


can not locate users manual, I think the service technician took it.
any idea where I can find one (manual in pdf format) online?

thank you for your responce
Roger @ ClicktoRemodel

 

 

yuri



142.161.75.21

"Re(5):Concord 80 plus oil furnace" , posted Sun 5 Oct 16:08user profileedit/delete messagepost reply


http://customer.honeywell.com/Business/Cultures/en-US/Default.htm

Snoop thru the residential products. There is a pdf file download area at the bottom of the products page once you locate your type

Yuri