Strange oil furnace problem - http://www.hvacmechanic.com/ Forums
Original message
| dbc120 | "Strange oil furnace problem" , posted Tue 7 Oct 23:33  
Furnace does not fire up initially. Meaning, it will and does fire up but only when I quickly flip the tstat switch from HEAT "on" to "AUTO" and even then it is sometimes? Blower works fine and did all summer with AC.
I have replaced the tstat thinking that was the problem but nope. All wires are tight to and from furnace/tstat that I have access to. I cleaned/replaced filters and even the nozzle. Put about $400 into service and parts end of last season. So not sure what the problem is? And yes...full tank of fuel oil. Rheem furnace with beckett burner. About 15 years old. Any advice is greatly appreciated. Thanks!
dbc120
| | Replies:
|
| djgilbert | "Re(1):Strange oil furnace problem" , posted Wed 8 Oct 06:41  
Some of those older rheems had a isolation relay right above the power junction box, usually on the right side, contacts in the relay could be dirty and relay may need to be replaced, could have loose connections
Don
|
| | dbc120 | "Re(3):Strange oil furnace problem" , posted Fri 10 Oct 14:50  
To those on here who tried to help me thanks but please take note and put in your memory bank in case this similar issue comes up again.
The problem which I solved after much more internet research and trouble shooting/problem solving had nothing to do with relay switches. It ended up being a $6 cad cell replacement. Unplugged old one plugged in new one (less than 1 minute) problem solved. I hope others can learn from this because I would start here next time because at $6 even if it is not the problem it doesn't hurt to replace these little things now and then.
dbc120
|
| | dbc120 | "Re(3):Strange oil furnace problem" , posted Fri 10 Oct 14:45  
dbc120
|
| jmar | "Re(1):Strange oil furnace problem" , posted Tue 7 Oct 23:57  
check fan switching relay to see if contacts are closing should read o across if closed, verafiy 24vac to t t at burner.
|
|
|
|  |
|