Goodman Heat pump Honeywell T stat - http://www.hvacmechanic.com/ Forums
Original message
| jbsac | "Goodman Heat pump Honeywell T stat" , posted Sun 12 Oct 15:43  
I have a goodman GSH14036 Heat pump and a AEPF426016 air handler, AC work great but trying to get the heater to work with a honeywell RTH7000 t stat. Wired at stat r-r/rc, o-o/b, y-y, g-g, c-blue, e- brown and aux- white, took off jumper in uint from y1-o, unit does not come on, with wire on unit comes on in cooling mode
jbsac
| | Replies:
|
| Houston204 
| "Re(1):Goodman Heat pump Honeywell T stat" , posted Sun 12 Oct 18:03  
You must also configure your new stat to match your system. Set option 170 to 7. 190 = 0 240 = 9
"Tip of the Day" Remember to remove power first.
|
| | jbsac | "Re(2):Goodman Heat pump Honeywell T stat" , posted Sun 12 Oct 19:49  
Houston204.... Thanks, I totally SPACED out about configuring the t stat. WORK GREAT......
jbsac
|
|
|
|