| Turboman | "air flow" , posted Thu 16 Oct 14:01  
I have forced air lp unit in new home my problem is that the house is 65 ft long and the furnace is located at one end and the two bedrooms at the other end of the house get quite cold if you keep the bedroom doors closed if you keep the doors open rooms seem to stay alot warmer. whats the problem and whats the best ways to fix? I live in Michigan
| | Replies:
|
| Freon | "Re(1):air flow" , posted Thu 16 Oct 16:04  
Most likely your problem is there is no way for the warm air entering those bedrooms to get back to (return to) the furnace. The fact the warm air can't escape the rooms (doors closed)means the air pressure in those rooms increases enough to make inflowing warm air decrease.
Easiest solution is cut the bottom of the doors. That way air can escape the rooms by flowing under the doors. Adding a true return duct to each room might be too expensive but would be the best solution.
|
|
|
|