Have a Lennox G43UF gas furnace that doesn't light?? I'm pretty much below novice level when it comes to furnace repair but here is what I do know. Tstat calls for heat and the unit begins the process. Led code is normal operation at this point. After approx. a minute it shuts down after not lighting. Led then codes no red, and a slow green flash which means pressure switch open, blocked inlet/exhaust vent or pressure switch closed prior to activating combustion. I have looked through window to see if there was any ignition and I saw nothing that resembled fire or hot. Am going to check pressure switch but I don't really know what to do with it. Checked gas supply and it should be getting gas?? Any thoughts or is more info needed?
OK, i found the pressure switch, but other than checking the 2 wires going to it and the connections, I can't find anything to do with it?? Thoughts? Thanks!!
[this message was edited by TedFred on Thu 16 Oct 18:11] | | Replies:
|
| theduke03 | "Re(1):Lennox lighting problems" , posted Thu 16 Oct 19:09  
It's never the pressure switch. Locate where air intake pipe connects to the burners. Dissassemble that connection and look for leaves clogging the screen. Check both vent pipes outside as well.