Achiever 90 won't light - http://www.hvacmechanic.com/ Forums


Original message

UnderAchiever90

199.120.96.82

"Achiever 90 won't light" , posted Sat 18 Oct 23:53user profileedit/delete messagepost reply


I have a Rudd Achiever 90 series. It iced up on me over the summer while using AC and got wet but AC still worked after I thawed it out. Turned on the heat the other day and nothing. I trouble shot it and found no spark. Took out the control board and was going to replace it. Noticed two resistors fried. De soldered and replaced resistors. Bingo I get Spark now! Still wont light a flame however. I am getting gas because I smell it after the start up cycle. Not sure what else to do. Any help would be appreciated.

 


Replies:

UnderAchiever90

199.120.96.82

"Re(1):Achiever 90 won't light" , posted Sun 19 Oct 19:25user profileedit/delete messagepost reply


I can get the furnace to run if I light it manually. But once its out thats it it wont restart. Should the spark be a continuous? It just sparks once on each cycle.