Honeywell RTH6300B and convector: heat problm - http://www.hvacmechanic.com/ Forums
Original message
| hoch | "Honeywell RTH6300B and convector: heat problm" , posted Mon 20 Oct 12:08:  
Recently I replaced an old Honeywell ChronoTherm with a Honeywell RTH6300B, wired to an apartment convector (blows air past cold water in summer, warm water in winter).
Red wire to R terminal (jumped to Rc) Blue wire to Y terminal White wire to W terminal (jumped to G) System Type Settings 1-0, 3-0, 5-5
This configuration worked fine for cooling. However on heat cycle it will not power on, either in AUTO or fan ON mode. I can get it to power on by shorting Y and R terminals so no electrical problems.
Am I missing something about the settings? Something incompatible about this model with a convector?
Thanks,
[this message was edited by hoch on Mon 20 Oct 12:10] | | Replies:
|
| techshawn | "Re(1):Honeywell RTH6300B and convector: heat " , posted Mon 20 Oct 19:28  
W is not supposed to be connected with G. G is fan terminal.
I like fixing everything.
|
|
|
|