| philzone | "rudd gass furence" , posted Tue 21 Oct 13:57  
i keep getting flame rollout switch code when heater tryes to start it would run for 30 secs then cut off but now nothing? any help?
PMC
| | Replies:
|
| techshawn | "Re(1):rudd gass furence" , posted Tue 21 Oct 18:58:  
1. reset rollout sensor. 2. restart furnace, watch if flame is rolling out of the chamber. 3. if rollout does happen, find out the cause( depressurized furnace room? clogged vent? whatever)
I like fixing everything.
[this message was edited by techshawn on Tue 21 Oct 19:04] |
| yuri 
| "Re(1):rudd gass furence" , posted Tue 21 Oct 18:57  
A flame rollout switch is a CRITICAL safety device. ANY time it trips the furnace should be checked by a pro for a cracked heat exchanger etc. Failure to do so may result in fire or CO poisoning!!
Yuri
|
|
|
|