"rudd gass furence" , posted Tue 21 Oct 13:57user profileedit/delete messagepost reply


i keep getting flame rollout switch code when heater tryes to start it would run for 30 secs then cut off but now nothing? any help?

PMC

 


Replies:

techshawn

70.52.160.10

"Re(1):rudd gass furence" , posted Tue 21 Oct 18:58:user profileedit/delete messagepost reply


1. reset rollout sensor.
2. restart furnace, watch if flame is rolling out of the chamber.
3. if rollout does happen, find out the cause( depressurized furnace room? clogged vent? whatever)

I like fixing everything.

[this message was edited by techshawn on Tue 21 Oct 19:04]

 

yuri



142.161.80.12

"Re(1):rudd gass furence" , posted Tue 21 Oct 18:57user profileedit/delete messagepost reply


A flame rollout switch is a CRITICAL safety device. ANY time it trips the furnace should be checked by a pro for a cracked heat exchanger etc. Failure to do so may result in fire or CO poisoning!!

Yuri